OCP for Tranformer secondary on a Construction Site Power Distribution Panel (Spider)

Status
Not open for further replies.

buzzr

New member
480vac1ph primary w/150amp CB. 120/208 vac secondary feeding 10 ea 20amp GFCI receptacles & 4ea 2/50amp power receptacles.
I know NEC 240-4 tells me I need to have the Secondary OCP (which the Manufacturer neglected to install) So can I install a fuse block in the secondary between the Transformer and the panel lugs. or do I have to install a fusable disconnect switch.

If I decide to install a circuit breaker and back feed the panel can I use a 150A breaker.

thanks
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would say that in this situation, 240.40 would require a disconnect.
As far as the breaker goes, a back-fed breaker would be permissible, but depending on your panel, a 150 amp may not be possible as a back-fed.. As far as the amperage we need more info such as transf. kva, etc.
 

iwire

Moderator
Staff member
Location
Massachusetts
I know NEC 240-4 tells me I need to have the Secondary OCP (which the Manufacturer neglected to install) So can I install a fuse block in the secondary between the Transformer and the panel lugs. or do I have to install a fusable disconnect switch.

If this is manufactured and listed equipment the NEC does not apply and you should not modify it.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
There's a mistake somewhere. You can not derive 120 pole to center, 208 pole to pole from any single phase source.
You can if it is (2) hot legs/conductors and (1) neutral coming from a wye connected source.

This voltage source is very common to individual apartments in a large complex.

I wish there was a 'better' name for it than single phase (although some utilities call this a network).
 

Electric-Light

Senior Member
You can if it is (2) hot legs/conductors and (1) neutral coming from a wye connected source.

This voltage source is very common to individual apartments in a large complex.

I wish there was a 'better' name for it than single phase (although some utilities call this a network).

That's not really single phase. OP said 480v single phase, meaning two wires.
He didn't say 480/277 two leg.
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
That's not really single phase.
It is often called single phase as there is a single L-L voltage. There is no official (i.e. industry standard like ANSI or IEEE) method for classifying this system. Personally, I will usually call it 120/208 1Phase 3 wire.


OP said 480v single phase, meaning two wires.
He didn't say 480/277 two leg.
I agree.
Based on only the OP, it is likely his secondary voltage description is wrong.
 