Strange voltages to neutral...

Status
Not open for further replies.

TRW0930

Member
Hello...got a small issue which is pushing me to the end...

3 phase with neutral-(575 between phases and what should be 347 phase to ground). What i'm getting is 575 between phases (good) but phase to ground is a little different A-G=440 B-G=440 and C-G=140 volts...everything seems to be running alright, just happend to come acrossed it today...any ideas would be great. Thanks
 
My guess would be that there is no system or main bonding jumper. The neutral is floating. What do you get for voltage when you check from neutral to ground?
 
this is not good

this is not good

met this before I beleive it is the neutral this can end up eventually in problems try to check connections as soon as possible
 