5-49 Log #3644 NEC-P05 Final Action: Accept in Principle
(200.8 (New) )
_______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Add new text to read as follows:
200.XX Common Neutral Conductors. Common neutral conductors shall not
be used unless specifically permitted elsewhere in this code.
Substantiation: It appears that CMP 2 is attempting to prohibit the use of
common neutral conductors by specifically permitting them in 215.4(A) and
225.7(B). There is no reasonable reading of the words “shall be permitted” that
can lead the code user to the conclusion that these words actually prohibit the
use of common neutral conductors in other cases. The act of specifically
permitting something in no way prohibits something else. Section 3.1.2 in the
NEC Style Manual says that the words “shall be permitted” are to be used to
permit an alternate installation method. The words “shall not” are required to
be used to prohibit an installation method per 3.1.1 of the Style Manual. This
change will make the wording in 215.4 and 225.7 comply with the style
manual rules. Also the prohibition of the use of common neutrals should rest
with CMP 5 as they have control of Article 200, Use and Identification of
Grounded Conductors and not with CMPs 2 and 4.
Panel Meeting Action: Accept in Principle
Revise the recommendation to read:
200.4 Neutral Conductors. Neutral conductors shall not be permitted to be
used for more than one multiwire branch circuit or for more than one set of
ungrounded feeder conductors unless specifically permitted elsewhere in this
Code.
Panel Statement: CMP-5 revised the proposal to more specifically apply to
multiwire branch circuits and feeders.
Number Eligible to Vote: 16
Ballot Results: Affirmative: 16
Comment on Affirmative:
JOHNSTON, M.: Continue to accept this proposed revision as amended by
the action of CMP-5. This additional section provides clarity to users about
how neutral conductors should be used and coordinates with the newly defined
terms neutral conductor and neutral point. Additional uses of the term common
conductor are not necessary and the NEC should migrate to removal of the
term as it is undefined and can cause inconsistency in enforcement.