Hi,
I am afraid I have a different opinion. Although the bulb may relative expensive than the tradition one, its average service life is 50,000 hs, which means you need not to change the bulb and it is totally maintenance-free. Besides, it does slash the bill if you change all the bulbs into LED one. I think the saving bills will compensate its cost.
http://assets.sylvania.com/assets/d...P XL.bc74ac49-8157-44fa-8138-461c57ffc768.pdf
Sylvania's super long life lamps are rated 50,000 hours at 12hr/day operation.
32W nominal
2950lm initial
2832lm mean (after about 20,000 hours of use)
2832/32= 88.5LPW, but it is
actually higher in actual use.
Looking at typical high performance RE80 curves, 90% maintenance.
This is no trickery, because published data is based on direct operation on 60Hz because that's just the ANSI testing standards. Actual use is at high frequency which actually improves the lamp efficacy. (60Hz magnetic ballasts are more or less obsolete)
GE-232-MAX-N+
100% output
61W input(30.5W/lamp)
2832 mean lumen = 93 LPW mean approx 87LPW at end of lamp life. 97 LPW when the lamps are new.
As you can see, they do not decay much.
LEDs rated for 50,000 hrs following LM-79/LM-80 standards means that LED's rated life is the point where the output has decayed 30% a VERY GENEROUS performance decay allowance which is about the same as metal halide.
So to even
equal fluorescent, a 5900 lumen LED system must:
1.) have mean system efficacy of 93 LPW and
shall not fall below 87 LPW by end of life.
2.) have an average life of 50,000 hours at 12hrs/day
3.) driver + LED module(s) can not cost significantly more than ballast + 2 fluorescent lamps
4.) provide light at 3,000K or 3,500K when specified without any compromise in efficacy
#1. Ain't gonna happen with LEDs we have today.
#3. Not just yet.
#4. Usually lower kelvin LEDs have lower LPW and highest LPW LEDs often have CCTs of ~6500K which nobody really wants