wireman1 Senior Member May 2, 2011 #1 the following electrical systems are used in a hospital normal power, alternate power[ genators ] ,critical care,life safety, and life support can any of the above be run in the same conduit or must all of them be run in seperate conduits ?
the following electrical systems are used in a hospital normal power, alternate power[ genators ] ,critical care,life safety, and life support can any of the above be run in the same conduit or must all of them be run in seperate conduits ?
roger Moderator Staff member Location Fl Occupation Retired Electrician May 2, 2011 #2 Read 517.30(C)(1) Roger
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer May 2, 2011 #3 And by the way, in terms of electrical requirements, the phrase "life safety" has meaning, but the phrase "life support" does not.
And by the way, in terms of electrical requirements, the phrase "life safety" has meaning, but the phrase "life support" does not.