WarrenG
Member
- Location
- Daytona Beach,Fl
Hello to all and thanx for any input on this matter. A customer just had a submerged encased well pump replaced, and also the control/starter box. The well pump requires single phase 230 volts to operate. The customer has a three phase 208/120 volt service. So a single phase 1kva pri 240 sec 32, buck and boost transformer was used to boost the 208 up to about 239 volt. The system worked fine for some time and then the transformer went bad, so they think. So a new exact replica was installed. Now the pump will not work at all. The voltage measured at the pump dissconnect is 239 volts before the pump is turned on. Once the pump is put in the on position, the voltage at the same dissconnect drop to nearly 0 or 7 volts. I did an amp check and amp draw is 0. There is no neutral in this system, its a 2 wire only with ground. I checked all the capacitors, overloads and contactor and wiring in the control box and everything seems fine. Even the coils of the motor were tested and they are within spec. Basically we start with 239 v untill the pump is put in the on position at which time it drops to 0 to 7. Any ideas whats going on here? Thanx for the help.