10-15 Log #267 NEC-P10 Final Action: Accept in Principle
(240.24(F))
__________________________________________________ __________
Submitter: Stanley J. Folz, Morse Electric, Inc.
Comment on Proposal No: 10-40
Recommendation: Text to remain as presented in the ROP.
Substantiation: The Panel action on this proposal should have been to Accept.
I am in agreement with the negative comment presented by Mr. Dollard. In
addition, the panel statement ?refer to CMP 1 for comment and switches are
permitted over steps?, was unresponsive to the submitter. Switches are not
electrical equipment and do not come under the rules of 110.26. 110.26 does
a good job of outlining clearances required for electrical equipment except
it does not address a panelboard on a stairway, i.e., there is no provision in
110.26 for a level work area. This is one of those common sense things. We all
know it?s wrong. Let?s say it.
Panel Meeting Action: Accept in Principle
Revise the recommended text in Proposal 10-40 to read as follows:
?240.24(F) Not located over Steps. Overcurrent devices shall not be located
over steps of a stairway.?
Panel Statement: The panel accepts the concept that overcurrent devices
should not be installed over the riser sections of stairways. However, many
stairways have horizontal landings that could prove suitable for installations
where appropriate working space exists. The prohibition of installations over
steps of a stairway satisfies the intent of Proposal 10-40 and Comment 10-15.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
Common Sense :roll: