I hope I cleared some things up. Thank you, Bob
Oh, no. Thank You, Bob. "Heh"
So, the open Wye is on the 14.4 kV side. And the utilization voltage side is a classic four wire three phase 240 Volt open delta with a grounded center tap on one transformer secondary.
Got it.
Here's the first thing I get. The fact that three buildings are supplied off this one transclosure rules out anything on the line side of the junction box where the separate building laterals are spliced.
This turns the focus to the machine shop itself. It sounds like something is being disturbed by the storms, for the correlation of the breaker trips with the storms to be something happening in fact.
The fact that the machine shop main breaker on the single phase panel and the other main breaker in the three phase panel have both tripped is still strange.
If I were able to be present, on site, I would be looking for what could be moved or shaken by the energy of the wind and sound in the storms, and I would be asking questions about the loads that commonly run, and were, in fact, running at the times of main breaker tripping.
I would also be asking if any branch circuit breakers operated at any time, in relationship to the main breaker trips.
The fact that both the three phase main and single phase main tripped is a cause for concern, based on what I understand at the moment.