 - New Jersey
 - Journeyman Electrician (retired)
In the 2011 NEC 422.31 has been re-written to include Appliances Rated over 300 VA and Motor Operated Appliances Rated Over 1/8 HP.  This eliminated the confusion generated by 422.32 which has been removed from the code text.
My question is regarding dishwashers, do they generally have motors rated at 1/8 HP or greater? If so then I'm asuming that breaker lock outs are out as the exception to a disconnecting means within sight.
422.31(B) Appliances Rated over 300 Volt-Amperes. For permanently
connected appliances rated over 300 voltamperes,
the branch-circuit switch or circuit breaker shall
be permitted to serve as the disconnecting means where the
switch or circuit breaker is within sight from the appliance
or is capable of being locked in the open position. The
provision for locking or adding a lock to the disconnecting
means shall be installed on or at the switch or circuit
breaker used as the disconnecting means and shall remain
in place with or without the lock installed.
Informational Note: For appliances employing unit switches,
see 422.34.
(C) Motor-Operated Appliances Rated over 1⁄8 Horsepower.
For permanently connected motor-operated appliances
with motors rated over 1⁄8 horse power, the branchcircuit
switch or circuit breaker shall be permitted to serve
as the disconnecting means where the switch or circuit
breaker is within sight from the appliance. The disconnecting
means shall comply with 430.109 and 430.110.
Exception: If an appliance of more than 1⁄8 hp is provided
with a unit switch that complies with 422.34(A), (B), (C), or
(D), the switch or circuit breaker serving as the other disconnecting
means shall be permitted to be out of sight from
the appliance.