Hello

I've got to install a 60amp circuit to a swimming pool panel. The inspector wants the 135' underground feeder to have an insulated ground and for it to be in PVC.

The supply house recommends aluminum Mobile Home Feeder Cable #s 2,2,4 & 6 because it is cheaper than copper THWN #4,4,4 & 8.

Will this mobile home feeder cable pull easily through such a long length of PVC? I've used it in 10' lengths of PVC but never 135' lengths.

Thank you for the great help.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Hello

I've got to install a 60amp circuit to a swimming pool panel. The inspector wants the 135' underground feeder to have an insulated ground and for it to be in PVC.

The supply house recommends aluminum Mobile Home Feeder Cable #s 2,2,4 & 6 because it is cheaper than copper THWN #4,4,4 & 8.

Will this mobile home feeder cable pull easily through such a long length of PVC? I've used it in 10' lengths of PVC but never 135' lengths.

Thank you for the great help.

UMM that would depend on the size pipe. I believe I used 1 1/2" and my 125' run went in like a champ.
 