R Rho_HV Senior Member Location Texas May 5, 2011 #1 I was wondering if NEC has any standards regarding spacing between uninsulated conductors of different potentials? Thanks
I was wondering if NEC has any standards regarding spacing between uninsulated conductors of different potentials? Thanks
iwire Moderator Staff member Location Massachusetts May 5, 2011 #2 LMAO said: I was wondering if NEC has any standards regarding spacing between uninsulated conductors of different potentials? Thanks Click to expand... Yes
LMAO said: I was wondering if NEC has any standards regarding spacing between uninsulated conductors of different potentials? Thanks Click to expand... Yes
R Rho_HV Senior Member Location Texas May 5, 2011 #3 iwire said: Yes Click to expand... where can I find it? What article?
iwire Moderator Staff member Location Massachusetts May 5, 2011 #4 I might be mistaken, I am not finding it.
david luchini Moderator Staff member Location Connecticut Occupation Engineer May 5, 2011 #5 See 366.100(E).