Hello,

A year or so ago I found in the code the allowable distance between the wall of a control enclosure and the termination side of the terminal strip I cannot find it again for some reason. I was wondering if you could lead me in the right direction? I am working in a control panel that has #8 awg wires landed on a terminal and there is maybe an 1-1/2" of room between the terminal and the enclosure...cant be allowable by code...right?

Thanks,
josh
 
I believe you want 312.6. It appears for a single #8, 1-1/2" is sufficient
 