Transformer question
Fordean
New Jersey
Electrical Contractor
Viewing a Transformer installed, Has 12250 volts approx. in / 480 out.
75Okva trans 6% imp.
I calculated 900 amp on 480 side. And label states that as well.
Service pulls 630 amps. on each phase +/- 30 amps.
High Temp on senso C phase is 110C. A = 95C, B = 97c.
Transformer c. I didnt right down.
On 480 side. They installed 1200 amp Main.
If the transformer is part of a NEC (as opposed to a POCO) arrangement the 1200 amp secondary meets NEC 450.3.
Conductor sizes, AIC rating, etc. not being considered.
OCPD or Temperature
OCPD or Temperature
Are you concerned about the breaker or temperatures?
110C is a tad warm for some transformers but not those with 150C rise design.
What is the transformer nameplate temperature rise?