Permanent Wiring used for Temporary
roger
Fl
Retired Electrician
Does anyone know if there is wording in any IBC section that prohibits using permanent conductors inside of permanently installed conduit raceways from serving temporary lighting?
Roger
I am not aware of anything in the IBC that prohibits using permanent wiring to supply temporary lighting.
Section 108.3 permits the building official to allow temporary power and electric supply to a structure before such installation is complete, but all wiring shall comply with the temporary power and lighting requirements of NFPA 70.
Chris
Chris
Thanks Chris, that is what I know as well, except that in the 2000 IBC it was 107.3.
There is a local inspector that is saying this on a job I am not actually involved with and I was not aware of anything, just curious and helping out.
Roger
Your welcome Roger.
It is interesting that the inspector is not allowing a permanent wiring method to be used to supply temporary lighting.
Chris
Your welcome Roger.
Chris
LOL Yeah one would think that permanent wiring is safer. Could it be that permanent wiring is not supposed to be energized until the final has been passed.
Your welcome Roger.
Chris
Isn't it though? :confused:
Roger
The permanent wiring method has more restrictions so it is probably safer than temporary wiring. I'm surprised he would make an issue of it. Did he cite a specific code violation? Also why can't you just call the permanent wiring temporary?
Dennis, this is a typical renovation job where portions of the building are being used daily. Some of the wiring will remain and other parts will eventually be removed so in reality the whole building is being operated with temporary wiring.
There are portions of the facility that are being wired for 480/277V but will operate temporarily under the existing 208/120V for quite awhile, I guess he will say all this wiring will have to be removed before changing from one system to another. ;)
I understand this same inspector has claimed this to be the case on other projects as well and I was wondering where he has come up with the notion.
Roger
I agree
So am I
As i said I am not directly involved but I have asked the parties that are involved to ask.
Because then it would have to be removed.
Roger
What would be the "unintended consequences" if someone calls this Rogue Inspector's boss? The guys sounds like he needs his wigns clipped. Without some code citation, does the inspector have any authority, the guy sounds like BArney Fife?
Rocky, I'm waiting to hear from the parties involved whether he can give them code article and section.
Roger