james_mcquade

Senior Member
Hi everyone.

I have a customer that wants to use #18 wire to power a 3/4 hp motor.
208 volts, 3 phase, neutral & ground. 10 amp breaker feeding a VFD powering the motor

I have always used #14 as the minimum.
Before i submit my report, i wanted to cite the code for the #14 wire size, but cannot locate it.

What is the minimum wire size allowed for powering a 3 phase motor?
Please cite the code, if i'm wrong, i would definitely like to know.
Since i cannot cite a code, all i can do at this point is make a recommendation.

Thanks in advance,
James
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Look at the conditions in 240.4(D)(1) and see if the installation complies.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
James don't let the customer dictate what you do. The only time I have seen wires that small were for the split system sanyo units with DC motors.
 

james_mcquade

Senior Member
Thanks for the replies.
Dennis,
I have a good relationship with this customer and he trusts me and my opinion.
I wanted to give him the code reference because one of the contractors on the bid list
has been, well lets say, been known to bend the rules and caused a lot of grief in the
past. They are having a hard time getting him off the bid list.

regards,
james.
 