1793

Senior Member
Location
Louisville, Kentucky
Occupation
Inspector
I have a 30a 240v feed out to a Tool Shed. Customer wants 4 circuit panel installed. Having to drive ground rod, where will I find the wire size needed from gnd rod to panel?

250.66 or 250.122

Thanks
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Also, extra ground rod and wire = $15.00 : meter to test = $$$$$$$

If the area is really easy to get 25 ohms with one rod and you are doing a hundred homes it may be worth it if the inspector doesn't make you prove each one to him/her.
 