Condition:
Five new shoulder to shoulder VFD's installed at plant approx 10-12' away from an existing yr 2000 vintage chart recorder. Chart recorder has two services to it, namely: 120V power (PH,Neut,gnd) and a shielded 4-20ma signal cable (no other cabling in conduit). 120V wiring fed from immediately adjacent panelboard, signal wiring fed from and instrument approx 150'away (instrument also fed 120V from a different panelboard we believe).
Motors are on average 125--250'' away, THWN wire, motors have well rated insulation (type F?), new VFD's have been fitted with dv/dt filters.
Issues:
Chart recorder goes wild when drives are operated, stopped or change speeds.
Fixes:
Grounding of upstream single phase transformer feeding the recorder panelboard checked ok. Chart recorder was fed with a double conversion UPS and behaved erratically when VFD's were operated.
We're trying caps on the signal wiring now.
Any situations similar to this one out there?
Thanks
Issues:
Fixes:
Thanks