Who knows the correct way to display this common secondary rating of a 3-phase transformer? My rule has always been to show the single phase power first followed by the three phase power.
220.5 Calculations.
(A) Voltages. Unless other voltages are specified, for purposes
of calculating branch-circuit and feeder loads, nominal
system voltages of 120, 120/240, 208Y/120, 240, 347,
480Y/277, 480, 600Y/347, and 600 volts shall be used.
Well speaking as a Senior Member of the Institute of Electrical and Electronic Engineers (IEEE), I will state that they have published an official ruling on this topic. But I don't know which it is, and I refuse to learn. :roll: If someone wants to look it up and post the official answer (and perhaps Jim has already done that), I will do my best to forget whichever is the official answer as soon thereafter as I can manage. I just don't think it is important to get this "right."![]()
According to the standards:
Three phase is shown with the L-L voltage first.
Single phase is shown with the L-N voltage first.
In real life anything goes, so I try to add Ph and W descriptors:
Three phase
480Y/277 3Ph 4W
208Y/120 3Ph 4W
240/120 3Ph 4w
Single phase
120/208 1Ph 3W
120/240 1Ph 3W
Well speaking as a Senior Member of the Institute of Electrical and Electronic Engineers (IEEE), I will state that they have published an official ruling on this topic. But I don't know which it is, and I refuse to learn. :roll: If someone wants to look it up and post the official answer (and perhaps Jim has already done that), I will do my best to forget whichever is the official answer as soon thereafter as I can manage. I just don't think it is important to get this "right."![]()
According to the standards:
Three phase is shown with the L-L voltage first.
Single phase is shown with the L-N voltage first.
In real life anything goes, so I try to add Ph and W descriptors:
Three phase
480Y/277 3Ph 4W
208Y/120 3Ph 4W
240/120 3Ph 4w
Single phase
120/208 1Ph 3W
120/240 1Ph 3W
This makes perfectly good sense, therefore it can't be correct. :grin:
I was at teh Home Depot and found plastic boxes for dryer receptacle that said ready for 220v, which isn't a standard NEMA voltage.
I take it people use whatever nomenclature they feel like using.