Chapter 9
Table 1 Percent of Cross Section of Conduit and Tubing for Conductors
Note(9) A multiconductor cable or flexible cord of two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that have elliptical cross sections, the cross-sectional area calculation shall be based on using the major diameter of the ellipse as a circle diameter.
How would I determine the conduit fill rate for type NM wire.....specifically 12/2 and 14/2 in 2 in rigid conduit?
334.24 Bending Radius.
Bends in Types NM, NMC, and NMS cable shall be so made that the cable will not be damaged. The radius of the curve of the inner edge of any bend during or after installation shall not be less than five times the diameter of the cable.
An maybe another problem, it's unlikely that you can maintain the required 5X bending radius when going through an LB conduit body.