How can i calculate 12v low voltage lighting for example MR16 12v 50w high hat
20 Can install i know 50/12= 4.1A at 12v i get about 83A in total of all 20 high hat how can i find out how much amp does each transformer draw from my 120v 15A breaker or would a 15A CKT work
I am not sure what formula you want. Are you thinking that 4 amps at 12v means that 20 fixtures would be 80 amps??? As trevor stated- simplest rule is that watts are watts so it is 50 watts at 120V = .4 amps for each one so 20 * .4 = 8 amps.
or
20 fixtures at 50 watt= 1000 watts. 1000/120= 8 amps
Again the actually usage will be a bit higher for the PF of the transformer.
Say your trany has a PF of .9. If the Watts is 50 then the VA (apparent or total power) would be 50/.9= 55.5 VA (true wattage used). The higher the PF the more real your wattage will be. Thus a .95 PF with 50 watt bulbs would be 53 VA.
As you can see even at 6 watts more for each can (20 cans) you would only have 120 watts more to the load.
Please correct me if I am wrong-- I know you will.....![]()
That helps i have another question may be you guys can answer it for me this is an example and i know the NEC don't allow it If i have 75W bulb at 120v total of 28 Can 75*28=2100W at 120V if i ran a 12AWG to my switch box and fuse it at 20A then split my light on Two switches 14 light per switch now using 14AWG splice to my 12AWG for light wip my 14AWG should not pull more than 9amp off each switch which mean my 14AWG Tap should be safe i can be wrong on this so correct if i am
20 cans at 50 watt is 1000 watts. The transformers have a PF but it would not affect it much in this case.