Do ___________ if service is > 120/240V, 800 amps, fed by a 150 KVA transformer

Status
Not open for further replies.

Electron_Sam78

Senior Member
Location
Palm Bay, FL
Has anyone come across a statement in the NEC or NEC Handbook that gives this limit (it doesn't have to be done if service is 120/240V, 800 amps, and fed by a 150 KVA transformer or less) on a recommended or required activity? I'm not sure what activity though. I thought it was doing an arc flash hazard analysis but the NEC doesn't cover that. Could that have come from NFPA 70E? Maybe it had to do with short circuit calculations but I'm coming up empty looking through the NEC Handbook. Did I dream this? :confused:
 

jumper

Senior Member
May be something to do with 240.4(C). IDK

(C) Overcurrent Devices Rated over 800 Amperes. Where
the overcurrent device is rated over 800 amperes, the ampacity
of the conductors it protects shall be equal to or
greater than the rating of the overcurrent device defined in
240.6.
 

jumper

Senior Member
Found a copy of it. 2009 NFPA 70E 130.3

Exception No. 1: An arc flash hazard analysis shall not be required where all of the following conditions exist:
(1) The circuit is rated 240 volts or less.
(2) The circuit is supplied by one transformer.
(3) The transformer supplying the circuit is rated less than 125 kVA.
 

Electron_Sam78

Senior Member
Location
Palm Bay, FL
Got it,

NFPA 70E section 130.3 Exception No. 1: An arc flash hazard analysis shall not be required where all of the following conditions exist:

(1) The circuit is rated 240 volts or less.
(2) The circuit is supplied by one transformer.
(3) The transformer supplying the circuit is rated less than 125 kVA.

That could be what I was looking for. It sounds a lot like it. I'm not sure where i got the 150 KVA and 800 amps.

Thanks for the help jumper :cool:.
 

zog

Senior Member
Location
Charlotte, NC
Found a copy of it. 2009 NFPA 70E 130.3

Exception No. 1: An arc flash hazard analysis shall not be required where all of the following conditions exist:
(1) The circuit is rated 240 volts or less.
(2) The circuit is supplied by one transformer.
(3) The transformer supplying the circuit is rated less than 125 kVA.

And that comes from IEEE 1584
 