Renewable_BG

New member
Does anyone have any information on Meggar (500V and 1000V) testing of new 1000V, 90C, PV Rated cables (short distances)?

I have tested AC MV cables in the past and have considered above 500Mohms as the standard of a good reading for new cables. Can the same standards be applied to DC rated conductors?

Thanks,
 

broadgage

Senior Member
Location
London, England
I dont see why not, there is no fundamental difference between the design and construction of AC or DC cables, and all common types are suitable for either system.
 

zog

Senior Member
Location
Charlotte, NC
Does anyone have any information on Meggar (500V and 1000V) testing of new 1000V, 90C, PV Rated cables (short distances)?

I have tested AC MV cables in the past and have considered above 500Mohms as the standard of a good reading for new cables. Can the same standards be applied to DC rated conductors?

Thanks,

ANSI/NETA testing standards have all the specs and testing procedires.
 