what is the 3 phase demand load in kw for 40 1 phase 5 kw dryers supplied by a 120/208v 3 phase 4 wire system.

I get 68.25kw like this: 40/3=14 dryers x 2 per phase = 28 dryers. 35-2.5=32.5%
28x5kw=140kw x 32.5%=45.5kw. 45.5/2=22.75 x 3 phases =68.25

The test book gives nearly three times this amount as an answer. Am I way off?
 

squaredan

Senior Member
Location
Pennsylvania
Dryer

Dryer

hey treyp3, I have been studying to take the test and doing alot of calculations and that is how i would do it...maybe we are both missing something...Dan did the question say anything about dwelling unit or commerical dyers cuz 220.54 is for dwelling units, same with Table 220.54 household dyers
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
what is the 3 phase demand load in kw for 40 1 phase 5 kw dryers supplied by a 120/208v 3 phase 4 wire system.

I get 68.25kw like this: 40/3=14 dryers x 2 per phase = 28 dryers. 35-2.5=32.5%
28x5kw=140kw x 32.5%=45.5kw. 45.5/2=22.75 x 3 phases =68.25

The test book gives nearly three times this amount as an answer. Am I way off?

How could it be 3 times your answer. If you just took 5000 * 40 = 200kw so it can't be correct.

I believe you are correct. I edited my work.
 
Last edited:

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
I agree with Dennis.

Going out on a limb, now, I'm going to say that if I were to do this problem I would do this:

40 dryers x 5kW = 200 kW
(now demand)
40 dryers = 23 + 17
17 x 0.5% = 8.5%
35% - 8.5% = 26.5%
200 kW x 26.5% = 53 kW

Note that I made no allowance for some dryers being on A*B, some B*C, and some C*A. My reason is because I do not see a panel schedule attached to the question, and I have no assurance that the load is evenly balanced. IMO, the "maximum load connected between any two phases" means exactly that - every dryer connected A*B, no balancing of dryers.
 

bob

Senior Member
Location
Alabama
what is the 3 phase demand load in kw for 40 1 phase 5 kw dryers supplied by a 120/208v 3 phase 4 wire system.

I get 68.25kw like this: 40/3=14 dryers x 2 per phase = 28 dryers. 35-2.5=32.5%
28x5kw=140kw x 32.5%=45.5kw
. 45.5/2=22.75 x 3 phases =68.25

The test book gives nearly three times this amount as an answer. Am I way off?

The 45.5 kw is the demand for the 40 dryers. No need to go any further.
45.5 kw/(0.208 x 1.73) = 126 amps.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I agree with Dennis.

Going out on a limb, now, I'm going to say that if I were to do this problem I would do this:

40 dryers x 5kW = 200 kW
(now demand)
40 dryers = 23 + 17
17 x 0.5% = 8.5%
35% - 8.5% = 26.5%
200 kW x 26.5% = 53 kW

Note that I made no allowance for some dryers being on A*B, some B*C, and some C*A. My reason is because I do not see a panel schedule attached to the question, and I have no assurance that the load is evenly balanced. IMO, the "maximum load connected between any two phases" means exactly that - every dryer connected A*B, no balancing of dryers.


George here is the issue I have with your calculation as I did the same thing. .5% should be taken on the total dryers used in the demand not the actual number (40) . We have a demand of 28 Dryers so we should be taking .5% of (28-23).

.5% of 5 not 17
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
George here is the issue I have with your calculation as I did the same thing. .5% should be taken on the total dryers used in the demand not the actual number (40) . We have a demand of 28 Dryers so we should be taking .5% of (28-23).

.5% of 5 not 17

Dennis, are you (and George) taking into account the last sentence in 220.54?
 

jumper

Senior Member
George here is the issue I have with your calculation as I did the same thing. .5% should be taken on the total dryers used in the demand not the actual number (40) . We have a demand of 28 Dryers so we should be taking .5% of (28-23).

.5% of 5 not 17

I am not seeing as how you came to this conclusion. I may be wrong, but I do not understand.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am not seeing as how you came to this conclusion. I may be wrong, but I do not understand.

Well article 220.54 tells us how to get the demand. there are 14 connections to 2 phases so the total number of dryers is based on 2 times 14 or 28.

We look in T. 220.54 and we see 35% minus .5% for each dryer over 23. If the demand is 28 dryers then we have 28-23= 5. We need to subtract .5% * 5 or 2.5% from (35% of the 200kw)

It seems if we are using that table at 28 dryers then why we we use that table and subtract 23 from the 40 dryers.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Well article 220.54 tells us how to get the demand. there are 14 connections to 2 phases so the total number of dryers is based on 2 times 14 or 28.

We look in T. 220.54 and we see 35% minus .5% for each dryer over 23. If the demand is 28 dryers then we have 28-23= 5. We need to subtract .5% * 5 or 2.5% from (35% of the 200kw)

It seems if we are using that table at 28 dryers then why we we use that table and subtract 23 from the 40 dryers.

George's math seems to be what table 220.54 says to do. 35%-0.5 x (40 dryers -23 = 17)=8.5. So 35-8.5=26.5%, then 26.5%x200 kva = 53 kva. You could also use each dryer at 5 kva. 5 kva x 26.5%=1.33 kva x 40 dryers = 53.20 kva. I'm not sure how the last sentence in 220.54 is used.
 

kwired

Electron manager
Location
NE Nebraska
Another thing to consider is the 5000VA rating of the dryer. This is likely the rating for 240 volts. If so, same unit operating at 208 volts is only about 3760 VA.
 

jumper

Senior Member
Well article 220.54 tells us how to get the demand. there are 14 connections to 2 phases so the total number of dryers is based on 2 times 14 or 28.

We look in T. 220.54 and we see 35% minus .5% for each dryer over 23. If the demand is 28 dryers then we have 28-23= 5. We need to subtract .5% * 5 or 2.5% from (35% of the 200kw)

It seems if we are using that table at 28 dryers then why we we use that table and subtract 23 from the 40 dryers.

I agree with George, NOPE.
 

kwired

Electron manager
Location
NE Nebraska
A dryer is not a purely resistive load, so are sure this is correct?

Inductive load is likely 1/3 - 1/2 hp so we are looking at what 4-600 VA for a motor and the other 90% or so of the load is resistive. Plus I said 'about 3670' and not 'is 3670'.
 