Look at the example for ranges in annex D. It is a 3 phase load feeding single phase ranges. Art. 220.54 says
That number is found by taking 40 and divide by 3-- we get 13 and a remainder of 1 so there are 14 ranges connected between any two phases-- this is assuming one is not trying to install them on the same phases.
Now we have 14 ranges but art. 220.54 states we double that number-- hence 28.
We are now working with 28 ranges not 40 except for the initial calculation of 40 * 5000 = 200 kw.
Now we take T. 250.54 for 28 ranges not 40. 35% of 200000= 70000. Now we must also minus .5% for each range over 23. Since we are working with 28 ranges we get 28-23= 5. 5* .5%= 2.5%. 70000 * 97.5%= 68, 250 or 68.25 kw
Where two or more single-phase dryers are supplied by a 3-phase, 4-wire feeder or service, the total load shall be calculated on the basis of twice the maximum number connected between any two phases.