EGC for Transformer Delta Secondary

Status
Not open for further replies.

beanland

Senior Member
Location
Vancouver, WA
13.09kV industrial feeder feeds a 1630kVA 13.09kV-575V delta-delta transformer. Transformer is protected by 15kV 100A current-limiting fuses. Transformer secondary (ungrounded) runs ~50 feet and feeds a 600V 2000A breaker. Because there is a delta winding, there is no neutral-ground bond at the transformer. A fault in the secondary conductors cannot create a line-ground fault because it is a delta winding. A line-line secondary fault will cause fuses to operate but cannot cause ground current. How is the EGC from the tranformer to the breaker sized. Do I install an EGC per 250.122 for a 2000A breaker? I know I can install in RGS or AL conduit to provide an EGC but what if part of the run is UG in PVC?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I would reference 250.30(B) and install a conductor based on 250.66
 