- Location
- Lockport, IL
- Occupation
- Retired Electrical Engineer
A new outdoor skateboard park will be lit by pole-mounted lights. I will mount a new 100 amp MCB panel on one of the poles. I will tap an existing transformer (300 KVA, 120/208V) and run an underground feeder to the panel. As I read the code, I will need a grounding electrode at the pole to which the panel is mounted, but not at any other light pole. That is because the first "structure" is served by a feeder, but each of the other lights will only be served by a single MWBC. Is that right? If so, can I use some aspect of the pole itself (presuming it is metal and is imbedded in a concrete base) as the grounding electrode, or will I need to install a pair of ground rods?