S soncarbes Member May 25, 2011 #1 if i have a 400 Amp service using 500 MCM what size grounding electrode conductor is required
roger Moderator Staff member Location Fl Occupation Retired Electrician May 25, 2011 #2 Have you looked at 250.66? Read the whole article not just the Table Roger
raider1 Senior Member Staff member Location Logan, Utah May 25, 2011 #3 What electrodes are you using? As Roger pointed out have you read 250.66? Chris
roger Moderator Staff member Location Fl Occupation Retired Electrician May 25, 2011 #4 These appear to be study questions and we will not just give you the answers, we will help you find the answers but you will have to do the work yourself. Roger
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) May 25, 2011 #5 Although you mention 500 kcmil and a 400 amp service keep in mind that the service size is irrelevant when using table 250.66.