RE:240.21 (C) (6) Calc

Status
Not open for further replies.

LYLE2231

Member
RE:240.21 (C) (6) Calc

Good Morning Friends, Could someone show/illustrate the calc for this article.
Thanks, Lyle
 
Good video, but, IMHO Mike kinda skimmed past the OP's calculation question.
I believe the situation to be as such:
Assume you have a 75 kva 3 phase 480/208Y1220 transformer with a 125 amp primary OCP device.
1/3 of the primary OCP device will be 42 amps.
The transformer ratio 480/208 is 2.31
42 amps X 2.31 is 97 amps so the minimum conductor ampacity would be 97 amps.

(I hope I did that correctly...the ratio throws me sometimes... if I'm wrong someone here will correct me)
 
Good video, but, IMHO Mike kinda skimmed past the OP's calculation question.
I believe the situation to be as such:
Assume you have a 75 kva 3 phase 480/208Y1220 transformer with a 125 amp primary OCP device.
1/3 of the primary OCP device will be 42 amps.
The transformer ratio 480/208 is 2.31
42 amps X 2.31 is 97 amps so the minimum conductor ampacity would be 97 amps.

Does anyone have an idea why we use this ratio?
 