200 amp sub panel equipment ground
Buck Parrish
NC & IN
I don't have my code book with me. A 200 amp sub panel fed with copper. Should that have a #4 or #6 copper equipment ground. I think it's 4, somebody is trying to tell me it's #6
I know the conductor to the cold water is #4
Nec 2008
All copper
Keep in mind that Section 250.22(B) would require a larger sized EGC depending on what size ungrounded conductors are used for that feeder circuit...
2/0 copper would not be sufficient for a 200A feeder unless the application you are referring to is the "main power feeder" per 310.15(B)(7) 2011 NEC. 3/0 conductors would be required at a minimum for a 200A general feeder per Table 310.15(B)(16)...
Thanks, I almost missed that. My OP is hypothetical. Again I don't have my book.
I'm on my Droid.
So with 3/0 is #6 still okay.
All copper, NEC 08
I'm on my Droid.
All copper, NEC 08
Yes....... The egc has nothing to do with wire size, unless you upsize, it has to do with breaker size.