aaronbailey52
It's not an NEC issue, but let's say I specified an insulated bonding backbone for my telecommunications spaces. Then let's say my contractor decided to strip off the last 18" of insulation for the leg between the EMT and the ground lug to save the trouble of running an additional bonding conductor back to serve the conduit. The wire exits the conduit through a grounding bushing. So, the wire is insulated while in the conduit, but then bare and exposed for 1-3 ft. Who can weigh in on this? I swear I found somewhere a distance limitation on bare ground wire in telecom spaces and the rationale for insulating said wires, but I cannot locate this. In my mind, stripping more than the minimum necessary insulation from the wire results in it no longer being an insulated wire and it should technically be replaced.