OK, It's been WAY too long since I had a class in magnetics.
I understand the basic reason for bonding both ends of a ferrous conduit when used for GEC is to eliminate the choke effect that is widely described in every NEC handbook However, 250.64E clearly states that the requirements apply to ferrous conduit only. Therefore, NO bonding would be required if the GEC was installed in rigid aluminum conduit.
So, what is unique about this effect and why does it apply with ferrous conduit only? Electrically, and magnetically, wouldn't rigid aluminum conduit functionally create the equivalent of a single-turn, shorted, air-core transformer secondary and therefore ultimately have the same "choke" issue? Obviously, magnetic fields can induce current in aluminum conductors and windings. Many (if not most) xfmrs now are manufactured with aluminum windings. Clearly, it must be due to the fact that ferrous conduit reacts to magnetic field and aluminum does not. However, since aluminum windings can still have a current induced into them from magnetic fields, I don't clearly see why the phenominia doesn't also occur with aluminum conduit.