beanland
- Vancouver, WA
Is there an article in the NEC that requires the installation of a grounded conductor (neutral) on the secondary of a grounded-wye transformer? If I install a step-down transformer with a grounded-wye secondary I am required to provide a equipment grounding conductor and grounding electrode conductor at the transformer neutral. Is there an NEC article that requires that I also install a grounded conductor (neutral)? There is an NEC article (230.42(C)) that requires a 250.66 sized grounded conductor for a service-derived source but I have not found the citation for the separately derived source. 250.30(A)(3) says "If a grounded conductor is installed..." which implies that it is optional.
Here is the dilemma: a PV system with grounded-wye transformer is connected to a service-derived grounded-wye system with phase-neutral load. The PV installer says that no neutral is required at their transformer. However, when operating in parallel, the PV system could supply unbalanced loads in the distribution system, leading to "neutral" current flow on the EGC because of the multiple neutral-ground bonds.
However, a neutral-ground bond at the transformer would pose a problem because there will now be multiple neutral-ground bonds in the system.
705.95 is not much help either because it does not cover 3-phase systems.
Is a neutral required? Is a neutral-ground bond required?