I guess I should have asked before I sent in a proposal but do you think that 250.122 (A) should be rewritten.  
It states, in no case shall the egc be required t be larger than the circuit conductors. If we install 7 conduits with1/0 conductors on a 1000 amp breaker then the egc is required to be 2/0 in each conduit. Do you all agree or disagree with me?
	
		
			
		
		
	
				
			It states, in no case shall the egc be required t be larger than the circuit conductors. If we install 7 conduits with1/0 conductors on a 1000 amp breaker then the egc is required to be 2/0 in each conduit. Do you all agree or disagree with me?
				