Where is the definition of 'convenience outlet?' A fair question. I would draw your attention to 210.21(B)(2), where branch circuits supplying two or more receptacles are discussed. I will concede that there is no reference to voltage.
Where does the NEC mention 'rolling around?' First off, my comment was in reply to another poster who described a situation where equipment was moved about in an industrial setting - I did not bring in that element. However, for your amusement, you might look at 210.19(A)(2), where there;s a reference to 'portable loads.'
The dryer + welder dilemma stumbles over the diverse nature of the loads. While we have general rules regarding sizing wire for ampacity, and breakers for overcurrent protection, in both cases the rules are severely modified for for these particular loads.
We 'forget' the nameplate of the dryer, and instal an already oversize 30-A circuit, using #10 wire. (Doing the math, we might be able to use a 25-amp breaker).
For the welder, we look to 630 ... and, by the time we're done, we might very well have a situation where code would allow us to use a 100-A breaker on #12 wires. It all depends on the nameplate of that specific welder- most notably on the 'duty cycle.'
Think about that for a moment. Fow the welder, #10 might be more wire than we must use, but that's a small small waste. Of greater concern is that 30-Amp breaker. That the NEC would allow a 100-Amp breaker for the welder suggests that ordinary welding activities can very easily lead to nuisance tripping of the 30-Amp breaker ... and we sure don't want to put the dryer on a 100-Amp breaker, do we?
Have a more capable welder, with a higher duty cycle, and the breaker sizing issue gets even worse. Remember: in welding a 'short circuit' is a good thing
I just don't see any way to reconcile the two different uses on one circuit. One feeder, yes ... one circuit, no.
Can you do it? Does it work? Is this the reasoning of someone so careful as to call 811 for a ground rod? Seems pretty daring to me.