Just reading my "Stallcups Electrical Calculations Simplified" and I've come across two examples that I find a little puzzling. Here's the first:
A store with an area of 6000 sq-ft is to have 90 lighting outlets
The load calculation is performed like this:
6000 x 3 = 18,000 VA
18,000 x 125% = 22,500 VA
90 x 180 = 16,200 VA
16,200 x 125% = 20,250 VA
The load is 22,500 VA based on the larger calculation.
However, NEC 220.14(I) state's that receptacle outlets are calculated on the basis of 180 VA per yoke. I was under the impression that with the exception of residences all receptacle loads are calculated separately from the lighting loads. Why is the book applying NEC 220.14(I) to lighting outlets?