D domnic Senior Member Occupation Electrical Contractor Jun 7, 2011 #1 IN a home built in 1960 a home inspector told the home owner the non gronded receptacles would need to grounded i cannot find this in the NEC.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jun 7, 2011 #2 to clarify, if you are referencing a two wire receptacle with no ground slot, you will find no NEC requirement to change it to a grounding type receptacle.
Ponchik Senior Member Location CA Occupation Electronologist Jun 7, 2011 #3 without knowing the details of the installation, the inspector is correct if the 2 wire circuit has a three prong receptacle on it.
charlie b Moderator Staff member Location Lockport, IL Occupation Retired Electrical Engineer Jun 8, 2011 #4 Take a look at 406.3. You will find evidence that the inspector is wrong.