Non grounded receptacles

Status
Not open for further replies.

domnic

Senior Member
Occupation
Electrical Contractor
IN a home built in 1960 a home inspector told the home owner the non gronded receptacles would need to grounded i cannot find this in the NEC.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
to clarify, if you are referencing a two wire receptacle with no ground slot, you will find no NEC requirement to change it to a grounding type receptacle.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
without knowing the details of the installation, the inspector is correct if the 2 wire circuit has a three prong receptacle on it.
 
Status
Not open for further replies.