 - Lockport, IL
 - Semi-Retired Electrical Engineer
I am circuiting concession stands for a minor league baseball field.  These clearly count as, ?non-dwelling unit kitchens.?  Article 210.8 (2008 NEC) does not distinguish simplex from duplex receptacles, so both will require GFCI protection.
The designer of the food service layout is calling for a number of simplex receptacles, usually of the type, ?NEMA 5-15.? Each item of equipment will get its own circuit. How do I GFCI-protect one of those? GFCI circuit breaker? Other options?
Also, the owner?s design basis guidelines state that all receptacles shall be rated for a minimum of 20 amps. So I have used 20 amp breakers and #12 conductors for all these circuits. But I can?t supply a NEMA 5-15, and no other load, from a 20 amp circuit. I intend to pass on to the food service equipment designer that they have to change their schedule to call for NEMA 5-20. Is this going to cause problems? Does this mean there will be additional costs for the equipment, since the equipment vendor needs to change out their plugs?