I am circuiting concession stands for a minor league baseball field. These clearly count as, ?non-dwelling unit kitchens.? Article 210.8 (2008 NEC) does not distinguish simplex from duplex receptacles, so both will require GFCI protection.
The designer of the food service layout is calling for a number of simplex receptacles, usually of the type, ?NEMA 5-15.? Each item of equipment will get its own circuit. How do I GFCI-protect one of those? GFCI circuit breaker? Other options?
Also, the owner?s design basis guidelines state that all receptacles shall be rated for a minimum of 20 amps. So I have used 20 amp breakers and #12 conductors for all these circuits. But I can?t supply a NEMA 5-15, and no other load, from a 20 amp circuit. I intend to pass on to the food service equipment designer that they have to change their schedule to call for NEMA 5-20. Is this going to cause problems? Does this mean there will be additional costs for the equipment, since the equipment vendor needs to change out their plugs?
The designer of the food service layout is calling for a number of simplex receptacles, usually of the type, ?NEMA 5-15.? Each item of equipment will get its own circuit. How do I GFCI-protect one of those? GFCI circuit breaker? Other options?
Also, the owner?s design basis guidelines state that all receptacles shall be rated for a minimum of 20 amps. So I have used 20 amp breakers and #12 conductors for all these circuits. But I can?t supply a NEMA 5-15, and no other load, from a 20 amp circuit. I intend to pass on to the food service equipment designer that they have to change their schedule to call for NEMA 5-20. Is this going to cause problems? Does this mean there will be additional costs for the equipment, since the equipment vendor needs to change out their plugs?