I see this as meritless. Back when 3 prong dryer receptacles were permitted and cabinet was bonded to neutral, a loss of neutral would cause the cabinet to become energized to 120v through the dryer's controls and motor.
Now that this isn't permitted, you'd need fourth wire for neutral.
You don't see condensing units with 240v compressor and 120v fan pulling from neutral to hot.
Even 1/25hp inducer motors, 75VA 24v control transformers in RTUs and blower motor in 240v window shakers are 240v and do not require a neutral.