PVC under cement floor
JGL63
Installing PVC below a commercial slab for the first time...does it go under the mesh? Do I need to trench or is the slab adequate cover? Any pointers?
Thanks!
GO BRUINS!!!
PVC in slab
PVC in slab
If it is a slab on grade I would go in the fill at least a few inches down. Less likely to have cracking along the pipe and prevents problems later when it's time for renovations that require floor cutting.
I agree under the mesh. I usually don't install much in the slab as I do residential work but I tend to wait for the stone then rake back a bit and lay my pipe, then cover it up. Usually the top of my pipe is flush with the stone.
I like to dig a trench. It keeps it down far enough and you can support it when you sweep up into a wall. If you have multiple PVC conduits coming up in the same area such as into a panel, use 2 pieces of 1/2 emt and tie them all together. Dont forget to cover the ends up. Objects fall inside. especially concrete
NEC wise you can lay it on the dirt and just cover it with the cement.
That said, look at your job specifications, I bet they tell you to have the conduits flush with or below the dirt under the slab as a conduit in a floor slab can result in a crack that follows the conduit.