Is the neutral to ground voltage in 480Y/277V and 208Y/12OV systems supposed to be 0? What happen if it is greater than 0? What is possible problem?

Thank you!
 
If there is any load on the system it will not be 0 due to voltage drop.

However is the difference starts exceeding say about 5 volts on a 120 circuit you may have other issues like open or unbonded neutrals.
 
Is the neutral to ground voltage in 480Y/277V and 208Y/12OV systems supposed to be 0?
At what point in the system? Presuming this is a grounded system, the voltage will be zero at whatever location (often the service panel) that you make the N-G bond. At any other location, as Bob pointed out, there will be some voltage drop along the neutral wire, and there will not be a similar voltage drop in the ground wire, so there will be a difference in potential (however small) between neutral and ground.

 
If there is any load on the system it will not be 0 due to voltage drop.

However is the difference starts exceeding say about 5 volts on a 120 circuit you may have other issues like open or unbonded neutrals.

If N-G voltage on 120V circuit is 11V (by metering), will this be a voltage drop issue?
 