A anbm Senior Member Location TX Occupation Designer Jun 14, 2011 #1 75kVA transformer (480V Pri - 208?120V sec) feed a panel with main CB. Can we bond neutral to ground at panel instead of xfmr and satisfy NEC?
75kVA transformer (480V Pri - 208?120V sec) feed a panel with main CB. Can we bond neutral to ground at panel instead of xfmr and satisfy NEC?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 14, 2011 #2 Yes. Your GEC would terminate there as well.
C cripple Senior Member Location Santa Fe, New Mexico Jun 14, 2011 #3 Grounding at XFMR Yes, if the secondary transformer are 25 feet or less. NEC 240.21(C) and 250.30(A)(1)
Grounding at XFMR Yes, if the secondary transformer are 25 feet or less. NEC 240.21(C) and 250.30(A)(1)