I know that some are rated NEMA 3R so those would be allowed.Is a wet location EMT connector allowed to enter the top of a NEMA III box? I can?t find where it is not allowed but I always thought a hub was required.
If you use sealing locknuts or myers hubs it would be compliant.
What about just the connector right out of the box? Don't they have a gasket or is something further required?
ETP makes a connector that is UL listed as raintight or wet locations 1/2"-2".What about just the connector right out of the box? Don't they have a gasket or is something further required?
.ETP makes a connector that is UL listed as raintight or wet locations 1/2"-2".
The last two brands I used came with a lock nut and a gasket.