10kw Generac 120/240v measured output 124,125, 248 (no load)
Loaded voltage 118, 118, 236 (at panel) Amperage 12-20.
Biggest load is a 1 HP water pump for a well.
300 watt APC UPS input voltage 115, output 117 (at unit 75' away)
Unit is clicking every 20-30 seconds (battery is discharging to bump voltage to 117)
Smart UPS does not have the problem It is 115 input, 115 output.
Have you experienced this? Is the small UPS defective?
POCO power is 112, 113, 225. This business is at the end of the line on poco grid. UPS does not do this while on POCO power only generator.
Thanks!
Thanks!