I did not look at it real good as I thought it did not concern me at rough. I think the plumber ran a flexible line to it. Unsure if that is CSST that you refer to?
For bonding of the conventional yellow- jacketed TracPipe? system, a bonding clamp must be attached to the brass AutoFlare? fitting adapter (adjacent to the pipe thread area – see Figure 4-21) or to a black pipe component (pipe or fitting) located in the same electrically continuous gas piping system as the AutoFlare? fitting. The corrugated stainless steel portion of the gas piping system SHALL NOT be used as the bonding attachment point under any circumstances. The bonding conductor shall be bonded per the National Electrical Code NFPA 70. Bonding electrode conductor sizing shall be in accordance with NFPA 70 Article 250, Section and Table 250.66
I have seen some CSST piping that requires the bond to be sized by T. 250.66.
Thanks Pete,
I have googled the issue and found much info about CSST & bonding. I have lots more understanding now than a few hours ago. I had no idea of the requirement as it seems it?s in the manufactures requirements of the plumber?s product. I guess I need a Ouija board up my ? BTW ?Experience is something that?s gained shortly after you really needed it.? Seems appropriate don?t ya think! Thanks again