roped conductors

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Conductors move during short circuits which can cause them to pull out of the lugs. Roping the conductors minimizes their movement.
 

Mike01

Senior Member
Location
MidWest
Roping

Roping

Like this (see attached)? This is definately not my handywork but I knew this photo would come in handy some day....
 

Attachments

  • 23040.jpg
    23040.jpg
    92.1 KB · Views: 0

squaredan

Senior Member
Location
Pennsylvania
Like this (see attached)? This is definately not my handywork but I knew this photo would come in handy some day....

Nice Rope Job..Is there a special way that they must be tied, where can you find this INfo? Also wanted to add that during a short circuit there is Major Magnetic forces, Expand and Collapsing, at work and those wires would just pull right out of lugs whip all around, thats why they use rope to tie them down...
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I saw this picture before, but I still don't understand how this would increase the withstand rating of the equipment from 10k to 65k.
Roping restrains the conductors movement, raising the amount of magnetic forces required before the conductors pull out of the lugs.
 

Mike01

Senior Member
Location
MidWest
Roping Mfgr. Requirements

Roping Mfgr. Requirements

You usually have to approach high levels of fault current before manufacturers require roping (around 85Ka for load cables and 130Ka for service cables) Typically (in my parts) we do not see fault currents of this magnitude (typically but I have in some locations) but when parallel generators or even large enough single gen sets start getting involved with closed transitions transfers, and main tie-main with closed transition transfers anything is possible. I have attached two images from a Square D catalog about roping see the table at the right for Ka requirements. It appears it does not "increase" the "withstand" rating of the equipment it is just a manufacturers requirement to help with movement and stresses created during a short circuit. So it does not increase the rating just helps deal with the conditions. Like a K rated transformer it does not mitigate harmonics just helps remove the excess heat created by the harmonics by utilizing more copper (or aluminum).
 

Attachments

  • sqd2.JPG
    sqd2.JPG
    83.2 KB · Views: 0
  • sqd_1.JPG
    sqd_1.JPG
    125.1 KB · Views: 0

squaredan

Senior Member
Location
Pennsylvania
You usually have to approach high levels of fault current before manufacturers require roping (around 85Ka for load cables and 130Ka for service cables) Typically (in my parts) we do not see fault currents of this magnitude (typically but I have in some locations) but when parallel generators or even large enough single gen sets start getting involved with closed transitions transfers, and main tie-main with closed transition transfers anything is possible. I have attached two images from a Square D catalog about roping see the table at the right for Ka requirements. It appears it does not "increase" the "withstand" rating of the equipment it is just a manufacturers requirement to help with movement and stresses created during a short circuit. So it does not increase the rating just helps deal with the conditions. Like a K rated transformer it does not mitigate harmonics just helps remove the excess heat created by the harmonics by utilizing more copper (or aluminum).

thanks Mike for the rope links!
 
HVAC zip ties

HVAC zip ties

Nice Rope Job..Is there a special way that they must be tied, where can you find this INfo? Also wanted to add that during a short circuit there is Major Magnetic forces, Expand and Collapsing, at work and those wires would just pull right out of lugs whip all around, thats why they use rope to tie them down...

The zip tie on that size wire will last 15 years or more I've used them and seen after that time they may become loss but the integrity is in tack. Never use rope.
 

stew

Senior Member
I have installed 4 ct cans in the last few years and all of them have instructions included with the can/service bussing that detail the size of rope (3/8) and number of wraps required regardless of loading.
 

iwire

Moderator
Staff member
Location
Massachusetts
regardless of loading.

The loading is irrelevant, it is the available fault current that would (or could) matter.

For instance you could have a section of switchgear with a 40,000 amp fault rating without roping but with roping it might increase to 65,000.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I meant to say fault current. The instructions with the service bussing never specified a fault current only that roping was required.

Yep. Just like Stew said, the diagram tells you to rope and how to do it. No mention of fault currents on the diagram.
 