brian john
 - Kilmarnock, Va
 - Retired after 52 years in the trade.
I have an existing facility with a single 750 KVA transformer 408 Delta 208/120 wye. The transformer was monitored for 30 days,  primary 45, secondary 1050 amps (rough numbers without puling up the report). This is a 30 year old dry type transformer and the customer is budgeting for replacement.  For the  primary overcurrent protection there is a 1200 amp FPE PL fusible switch and the secondary is a 2000 amp switchboard with a single fusible main.
Here is the issue, a new 750KVA and/or a 500 KVA transformer will not fit down the hall or into the electric room, no how no way without doing major structural changes. What I have thought about would be paralleling 2-250 KVA transformers. But I am not clear on the NEC on this. Could I utilize a single overcurrent protection device on the primary or do I need separate OCP for each transformer? Could I legally parallel the secondary to the line side termination connections 2000 amp switchboard main if the existing OCP was properly sized.
In lieu of this I would have to install 2 separate transformers with individual OCP and secondary switchboards which goes back to the initial problem of getting this equipment into a facility and the resultant extended outage. This is a 24x7 facility.