I am looking for a code article for how much phase tape is needed when you re-identify ungrounded conductors. Somewhere 6" comes to mind but I can't find it in the code.

Thanks in advance
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I am looking for a code article for how much phase tape is needed when you re-identify ungrounded conductors. Somewhere 6" comes to mind but I can't find it in the code.

Thanks in advance

You won't find a specific length of phase tape required in the NEC.