Tried to do the right thing; got hammered instead
Not trying to beat you up but,
  • What is a "service sub-panel"?
  • The connection for bonding a water piping system does not have to be within 5' of the entrance, see 250.104
  • Was the gas piping just being bonded per 250.104?
  • Why would a supplemental grounding electrode (or as Hendrix questions, any grounding electrode) be needed for a sub-panel?
Roger
250.52 A 1. 2008
As for the distance a water pipe can be used as a GE
250.52 A 1. 2008
That's correct but, I was not addressing it as a GE, the OP hadn't explained that this was a detached building needing it's own GES at the time.
Roger